Load side line side service disco confusion

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Attached sketch shows incoming service conductors into 1600A main service disconnect. From the 1600A main service phase conductors plus equipment grounding conductors go into trough from which their is a tap to POCO meter then to disconnects #1 to #9 as shown which are either 200A or 100A disconnects. The disconnects feed each tenant.

You see all things up to to meters have POCO lock and may be controlled by POCO making it difficult as to what is line side, load side, service disconnect and location of main bonding jumper(s).

Questions are:

1. What is considered load side and what is considered line side for application of 250.24(A)(5)?

2. Which is service disconnect 1600A switch only or 1600A and #1 to #9 disconnects are all service disconnects?

3. Should main bonding jumper be at 1600A switch only or at 1600A and disconnects #1 to #9? I am aware of 250.24(B) and definition of service NEC Article 100 however not sure what is the service disconnect in this case.
 

Attachments

  • B457683D-4866-420D-8EDC-5DC43B818692.jpeg
    B457683D-4866-420D-8EDC-5DC43B818692.jpeg
    73.7 KB · Views: 19
Last edited:
Do any of the disconnects (i.e., the 1600A and items 1-9) include overcurrent protection (i.e., are they fused switches)? The "service point," which is the boundary between line side and load side, will be at the first OCPD. I strongly suspect that is at the 1600A switch, and that that switch includes overcurrent protection. Otherwise, you have more than 6 disconnects needed to shut off power to the facility.
 
Do any of the disconnects (i.e., the 1600A and items 1-9) include overcurrent protection (i.e., are they fused switches)? The "service point," which is the boundary between line side and load side, will be at the first OCPD. I strongly suspect that is at the 1600A switch, and that that switch includes overcurrent protection. Otherwise, you have more than 6 disconnects needed to shut off power to the facility.

Yes 1600A switch has 1600A fuse in it, items #1 to #9 disconnects has either 200A fuse or 100A fuse in it.
 
With the meters being located on the load side of the 1600a Main Disconnect this is merely a stick built version of a group metering setup with a main the terminal box.

I'm curious as to how they made the taps from the 1600a conductors to the individual meter bases.