Doesn't sound like the is overcurrent protection at the meter. If there is no OCPD at the meter then conductors cannot run through the attic unless they're encased in concrete.Do the load side conductors off of the meter, feeding a panel, need protection crossing over another dwelling in an attic, like in a 4-plex, or can you just use SE cable?