Load testing a GFCI protected conductor

Status
Not open for further replies.

ELSLI

New member
Location
Medford,NY,USA
Scenario: A pool filter is tripping a 240V single phase GFCI Breaker. The breaker holds with no load on it.

Can any one suggest a good way to load test the conductors and breaker to rule them out as the cause of the problem. I don't like telling a homeowner to get a pump serviced or replaced if the problem is with the circuit.

I considered a 240V electric heater, not the most efficient thing to carry on a truck. I feel a load test on the conductors is the best test to rule them out. If the breaker still trips then I would suspect a conductor is failing under load.

Perhaps I am thinking this through wrong.
Thanks for any suggestion.
 
Scenario: A pool filter is tripping a 240V single phase GFCI Breaker. The breaker holds with no load on it.

Can any one suggest a good way to load test the conductors and breaker to rule them out as the cause of the problem. I don't like telling a homeowner to get a pump serviced or replaced if the problem is with the circuit.

I considered a 240V electric heater, not the most efficient thing to carry on a truck. I feel a load test on the conductors is the best test to rule them out. If the breaker still trips then I would suspect a conductor is failing under load.

Perhaps I am thinking this through wrong.
Thanks for any suggestion.

Can you temporarily move the water heater to the pump breaker and just dump some hot water until it cycles on. You could also throw a megger on the truck. Takes up less space then a heater. :roll:
 