Senior Member
Do they make a 175 amp snap in breaker for a load center. I have a situation where this site has a 200 amp panel on the outside of a storage shed. They want to feed a new structure with 175 amp breaker from this panel. The panel now only has 2 outside 20 amp gfi on it now. Do I have to change the load center panel to a 200 amp disconect put a trough then subfeed the two panels ? or change to a panelboard that accepts a 175 amp breaker?
 
What type breakers are in there now? QPP, QPPH, HQPP, HQPPH, etc?? How many poles? What interuption rating do you need?
 
101010 said:
Do they make a 175 amp snap in breaker for a load center. I have a situation where this site has a 200 amp panel on the outside of a storage shed. They want to feed a new structure with 175 amp breaker from this panel. The panel now only has 2 outside 20 amp gfi on it now. Do I have to change the load center panel to a 200 amp disconect put a trough then subfeed the two panels ? or change to a panelboard that accepts a 175 amp breaker?

I bet that the loadcenter says maximum 125 amp breaker on the buss bar
 
Your probably right. I quess the easiest way is to install a 200 main disconnect with 2 lugs on load side then sub-feed new panel as well as existing panel. might be cheapest way also.
 
Maybe Siemens makes a 175 amp feed-through panel and you can just swap the guts over. I know they make a 200 amp feed-through but don't recall if it's the same size as their typical 200 amp loadcenters. If you can swap guts, that wouldn't be to bad.
 