Continuous Load. The total load on any overcurrent device located in a panelboard shall not exceed 80 percent of its rating where, in normal operation, the load will continue
for three hours or more. Exception: An assembly, including the overcurrent device,
shall be permitted to be used for continuous operation at 100 percent of its rating where it is listed for this purpose.
Sorry, but that is in the ?construction specifications? area. I don?t think article 408 will help. It just talks about the ratings of the panelboard, and about protecting the panelboard. The issue here is protecting branch circuits. That is in 210.Originally posted by wirenut1980: Don't have a code book with me, but I think 408.36 applies in the NEC
I agree. 210.20(A).Originally posted by jtester: I believe that the 80% applies to continuous loads. I don't think that there is anything wrong with loading a breaker to more than 80% if the load is not continuous. That would apply to a branch breaker as well as a panel main breaker.
Jim T.
I agree that it is allowed by Code. But is it a good design practice? IMO, no it's not.Originally posted by charlie b:
Jim T.
Thats great if the customer wants to pay for that, if we are taking about adding a few more 20 amp branch circuits the cost is not a big deal.Originally posted by rr:
I use the 80% rule on all of my designs. Why? Because we have no idea what the customer load is going to be if equipment is changed, moved, or modified once the engineering has been completed.
Originally posted by iwire:
School construction is performed this way. Practically 100% of the time, schools will expand for future relocateable classrooms, ballfield lighting and other additional equipment. The schools don't have the budget for everything on their wish list, but they sure want the capacity there for future additions.Say you do you NEC load calculations and find the NEC allows a 1000 amp service. Now you apply your '80% rule' and the service jumps up to 1250 amps which is not a standard size. The next standard size is 1600 amps. Now we have a 1600 amp service where a 1000 would have been fine and the real kicker is it is highly likely the utility company will consider the load to be 500 or 600 amps.
True and it's a common problem trying to explain this to a customer. For example, if they have plans for future additions or equipment, I always try to explain to them that it's cheaper to have it done during the initial construction phase. Downtime as a result of additional/modified branch circuits, panelboards and transformers might be costly. And let's not forget about the labor of cutting, drilling, coring, patching and painting that's involved. Yikes!IMO good engineering looks at each installation individually, a one size fits all approach may work but it also will cost the customer money they do not want to spend at this time.