Loading for Fixed Multioutlet Assemblies

Merry Christmas
Status
Not open for further replies.

drmeyer

Member
Can anyone elaborate on the Code implications of adding Fixed Multi outlet Assemblies(6 receptacles that plug into a duplex receptacle) to a hotel room occupancy. Does the availability of additional receptacles violate the loading of individual circuits?
 
Re: Loading for Fixed Multioutlet Assemblies

It is still a single outlet with a listed assembly used within its listing. Granted, there is more of a chance of overloading the receptacle but these are used for plugging in lamps and the occasional computer and peripherals. I do not believe there is much chance of an overload. :D
 
Re: Loading for Fixed Multioutlet Assemblies

Thanks, Charlie. Yes it is a listed outlet. I was concerned that the load calculation would change and I might run afoul of the code. I realize that there is a greater possibility of overloading a circuit, but I'm counting on diversity.

Thanks for your comment.

Don
 