Loading for Fixed Multioutlet Assemblies

Status
Not open for further replies.

drmeyer

Member
Can anyone elaborate on the Code implications of adding Fixed Multi outlet Assemblies(6 receptacles that plug into a duplex receptacle) to a hotel room occupancy. Does the availability of additional receptacles violate the loading of individual circuits?
 
Re: Loading for Fixed Multioutlet Assemblies

It is still a single outlet with a listed assembly used within its listing. Granted, there is more of a chance of overloading the receptacle but these are used for plugging in lamps and the occasional computer and peripherals. I do not believe there is much chance of an overload. :D
 
Re: Loading for Fixed Multioutlet Assemblies

Thanks, Charlie. Yes it is a listed outlet. I was concerned that the load calculation would change and I might run afoul of the code. I realize that there is a greater possibility of overloading a circuit, but I'm counting on diversity.

Thanks for your comment.

Don
 