After applying the derating factors for temperature, and number of conductors in a conduit, do you reduce the load to match the ampacity or reduce the breaker size, or increase the wire size?

[ July 07, 2003, 10:49 PM: Message edited by: bennie ]
 

bennie

Esteemed Member
Re: Loading

Hi Web: If you increased the wire size from No.#14 to No.#12 because of derating, could you put the No.#12 on a 20 amp breaker?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Loading

The use of the term "derating" is misleading. The correct code term is "ampacity adjustment". If the ampacity of a conductor is required to be adjusted because there are more than 3 current carrying conductors in a raceway or because of an ambient temperature above or below 30?C, then the "adjusted ampacity" becomes the maximum code permitted ampacity for that conductor and the overcurrent protection device is not permitted to exceed the "adjusted ampacity" in most cases.
Don
 

bennie

Esteemed Member
Re: Loading

I have always been under the impression that load is adjusted to meet the corrected ampacity, or the the size of the conductor is selected to meet the load after correction factors are applied.

The overcurrent device is sized to the ampacity, without the correction factor. 240.4(D)
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Loading

Bennie,
I have always been under the impression that load is adjusted to meet the corrected ampacity, or the the size of the conductor is selected to meet the load after correction factors are applied.
In most cases the load is fixed, so the conductor is sized so that the (adjusted) ampacity of the conductor equals or exceeds the load and the conductor is protected at or below its ampacity.
The overcurrent device is sized to the ampacity, without the correction factor. 240.4(D)
The code section is poorly worded, but I don't read it as saying that you can protect these small conductors with an OCPD that a rating higher than the adjusted ampacity.
Don
 