Let me run this by you Guys.
A 30 Hp Motor (480VAC Nameplate FLA 35A) run off a 40 HP VFD (Continuous 30HP max 59A out) with the motor about 3 feet above and 3 feet behind the Control Panel. (clearly visible/ line of sight from the control panel).
Control System / Wiring all internal to Panel.
A 100A circuit breaker feeding a Power Distribution Block to a set of 80 Fuses (59a * 1.25) for the VFD and also feeding a set of fuses for a 5KVA 480/120 VAC 1PH transformer (to small controller).
Would using a through-the-door disconnect switch or maybe even a cable operated disconnect switch (lockable) on the 100a breaker, be a NEC legal move?
A 30 Hp Motor (480VAC Nameplate FLA 35A) run off a 40 HP VFD (Continuous 30HP max 59A out) with the motor about 3 feet above and 3 feet behind the Control Panel. (clearly visible/ line of sight from the control panel).
Control System / Wiring all internal to Panel.
A 100A circuit breaker feeding a Power Distribution Block to a set of 80 Fuses (59a * 1.25) for the VFD and also feeding a set of fuses for a 5KVA 480/120 VAC 1PH transformer (to small controller).
Would using a through-the-door disconnect switch or maybe even a cable operated disconnect switch (lockable) on the 100a breaker, be a NEC legal move?