Hello all,
I just recently joined the forum to submit a query about a recent installation that failed inspection. I have on countless occasions used this forum for code interpretation, general knowledge and many other situations to help become familiar with different opinions and resolutions to challenging electrical questions. If I’ve learned anything in this trade the past 15 years, its knowing that you will never stop learning!
On to my question/situation...
I recently completed a relatively straightforward installation of a 400 amp overhead service upgrade for a client. The existing 200 amp service became inadequate after the client added an additional 200 amp panel for a 3000 sq. Ft. wood working shop on his property. Load calculations and all are irrelevant to the main issue. Long story short- I installed a new 400 amp meter, overhead mast, etc. With 2 200 amp service disconnect/panels adjacent to eachother, and the 400 amp meter furthest to the right hand side.
The subject was brought up in this thread with the graphic that depicts my install almost identically:
Previous Thread
So install is complete and inspection is called in. The inspector comes out and fails me for 312.8(A)(3). More specifically, I labeled the feed through enclosure ”feed though conductors originate in meter enclosure and terminate in adjacent panel”. Evidently, because the code language in 312.8(A)(3) specifies “disconnect”, service conductors can not be fed through one enclosure to feed another with a disconnecting means.
Ive used this method on other installations as well, where the practicality of putting the meter in the middle just wasn’t going to work and had no problems with inspection. I discussed the issue with both the inspector and the head inspector whom both told me that this problem came up recently in a meeting and “this” was their interpretation to the problem.
Personally, I don’t understand the problem since service disconnects will always have energized conductors while the POCO meter is in place. Perhaps something that should be amended or changed for clarification in the future?
I just recently joined the forum to submit a query about a recent installation that failed inspection. I have on countless occasions used this forum for code interpretation, general knowledge and many other situations to help become familiar with different opinions and resolutions to challenging electrical questions. If I’ve learned anything in this trade the past 15 years, its knowing that you will never stop learning!
On to my question/situation...
I recently completed a relatively straightforward installation of a 400 amp overhead service upgrade for a client. The existing 200 amp service became inadequate after the client added an additional 200 amp panel for a 3000 sq. Ft. wood working shop on his property. Load calculations and all are irrelevant to the main issue. Long story short- I installed a new 400 amp meter, overhead mast, etc. With 2 200 amp service disconnect/panels adjacent to eachother, and the 400 amp meter furthest to the right hand side.
The subject was brought up in this thread with the graphic that depicts my install almost identically:
Previous Thread
So install is complete and inspection is called in. The inspector comes out and fails me for 312.8(A)(3). More specifically, I labeled the feed through enclosure ”feed though conductors originate in meter enclosure and terminate in adjacent panel”. Evidently, because the code language in 312.8(A)(3) specifies “disconnect”, service conductors can not be fed through one enclosure to feed another with a disconnecting means.
Ive used this method on other installations as well, where the practicality of putting the meter in the middle just wasn’t going to work and had no problems with inspection. I discussed the issue with both the inspector and the head inspector whom both told me that this problem came up recently in a meeting and “this” was their interpretation to the problem.
Personally, I don’t understand the problem since service disconnects will always have energized conductors while the POCO meter is in place. Perhaps something that should be amended or changed for clarification in the future?