Construction is ten years old. Secondary is 277/480.
Wire size 500mcm cu., single run X 4 conductors plus EGC.
Length is 750', yes 750'.
No pull box in that 750'.
1 phase trips instantaneously and another trips out after a few minutes.
Customer wanted to pull the one conductor out of the conduit and replace that one conductor somehow. Today they are willing to pull the entire run, replace the blown out conductor and repull.
All seems like bad ideas to me.
We want to identify the location of the fault, dig up, cut pipe and wire, then add splice boxes necessary.
With the equipment we have, there doesn't seem to be a good method to locate the fault inside the conduit that would provide enough confidence that we were right before we start digging. At MV we just thump. Our thumper won't get below 4K.
What methods have you seen work? Maybe you can offer other options.