Doing a resi service and panel upgrade 100->200.
I always upgrade the grounding system with 2 rods as I don't trust old metallic water pipes and I'd need to supplement anyways.
I also need to install the IBT.
Meter and panel locations must remain as drawn.
Question:
1) Can one simply install the IBT into a non-concentric 1/2" KO in the bottom of the meter base and leave it like that? [250.94(A)(4)]
2) Must I also bond it to the house panel's ground bar where the GEC is terminated? [Will do this anyways]
3) Or must it be part of the continuous #6 GEC? [250.94(A)(5) says "...or to the GEC with a #6]
My confusion is that between NEC numbers 4 & 5 in that article there seems to be a lot of options, and (A) states ...it SHALL comply with the following [1-6], not some, but all.