Do the lights and smoke alarms need to be Arch Faults.I realize the outlets need to be.
Thanks Rick
			Thanks Rick
This has been a matter of some discussion on this forum, and there is not a universal agreement. Here is my interpretation:Originally posted by bthielen: Am I correct that an "outlet" includes light fixture boxes, switch boxes, and receptacle boxes alike
Kirchoff tells us that the sum of the currents about a point is always zero. The current(s) in added to the current(s) out equals zero.Switches are not normally current using devices. . .
Outlet. A point on the wiring system at which current is taken to supply utilization equipment.
I don't agree with Tom on this one. The current is not taken to supply utilization equipment at the switch location. The current is taken to supply the utilization equipment at the point where the utilization equipment is connected to the wiring system. In the case of a lighting circuit, this point is at the light fixture, not at the switch that controls the light fixture.As Tom Baker states in the AFCI Confusion thread, "A switch is installed at an outlet."
I could be wrong, but I don't think there is. The only change I am aware of to 210.12 is the 6 foot from the panel rule when the conductors are in a metal wiring method.Originally posted by tom baker:
Don you are right, but I explain this the same way Mike Holt does. Isn't there a code change for the 05 cycle on the issue of a switch not having to be AFCI protected?
Directly is what mucks this up for me. I understand other's reading of outlet to be: the current leaves the wiring system and enters the utilization equipment without re-entering the wiring system and returns to the wiring system only after leaving the utilization equipment.If it does not directly supply power
What is that explanation, Tom?. . .either yours or Mike's? I must be misunderstanding what you meant. Is Mike's illustration 210-4 in his Illustrated Changes to the NEC? - 2002 Edition, page 27, where two snap switches, a dimmer switch and a fan speed control are called out (labeled) as "Switch Outlets" what you are referring to?Originally posted by Tom Baker
DonOutlet. A point on the wiring system at which current is taken to supply utilization equipment.