jbt260

Member
Location
Ohio
Occupation
Electrical Engineer
I have a customer owned 2300V-480/277V outdoor transformer fed from the customer's 2300V distribution. The secondary conductors run underground approx 200' then enter the lower level of a building then up one floor to the main breaker.

My question is: How far can I run inside the building from point of entry to the main breaker? Or do I need O/C protection right at the point of entry, or even outside prior to entry?

Thanks,
 
It may also be up to your local codes. In my state, the limit is 15 feet. I don't know if Ohio has its own limit. The NEC does not give a limit. But I have taken advantage of the rule that says the conductors are still "outside the building," if you surround them with 2 inches of concrete.
 