Can an electrical panel located in one office suite (Different business's) feed another separate office suite by code?
There is maintenance staff able to access the business where the panel is located.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
No. 240.24(B). There are two "unless otherwise" paragraphs, and your situation does not fit in with either one of them.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Can an electrical panel located in one office suite (Different business's) feed another separate office suite by code?
There is maintenance staff able to access the business where the panel is located.

sure. as long as there is some provision for ready access to the panel. could be as simple as having a key available in some way.
 