Re: location of disconnects
I have seen installations where the disconnect feeding the VFD or start/stop switch is remotely located and is capable of being locked in the open position.
Herve, as you state that this is a "production facility", I assume that it is an industrial facility. You are correct, provided that this lockable VFD(controller) disconnect mechanically opens all ungrounded conductors (a lockable start/stop selector switch by itself controlling a contactor coil would not be suitable.) In an industrial facility, where the "controller(in this case, VFD) disconnecting means" is lockable and disconnects all three phase conductors, the normal installation method would be to also use it as the "motor disconnecting means." A separate local disconnect at the motor would not be required due to exceptions allowed under 430.102 (B)(b)
ART 430.102
Under 600v the controller diconnecting means must be within sight(and less than 50 ft per definitions) of the motor controller per 430.102(A). The controller is not required to be in sight from the motor.
The controller disconnecting means shall also be permitted as the motor disconnecting means 430.102(B)
The motor disconnecting means shall be "in sight" of the motor. See exceptions under 430.102(B) that would allow motor disconnecting means to be out of sight of he motor. (a)...impracticle, additional hazards...
(b)...industrial...where conditions of maintenance and supervision ...
Either of these exceptions, if applicable, would allow one lockable disconnect to serve as both controller and motor disconnect while not in sight of the motor.
Suggest to your contractor to read 430.102 more thoroughly.
Len