Location of Grounding Electrodes (ground rods)

Status
Not open for further replies.

Ben_b

New member
Im upgrading a service in which the only grounding electrode is the water main. Where the location of my service is there is no safe location to drive the ground rods. My question is what is the maximum distance from the service to the grounding electrodes?
 

hillbilly

Senior Member
You have to bond to that water pipe within 5 feet of where it enters the building.
250.52(A)(1).
As Iwire said, the NEC doesn't give a maximum distance from the service panel to that "5 foot section" of pipe.
steve
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
hillbilly said:
You have to bond to that water pipe within 5 feet of where it enters the building.
Only if you want the pipe to qualify as an electrode. The bonding requirement does not specify where on the piping system.
 

hillbilly

Senior Member
LarryFine said:
Only if you want the pipe to qualify as an electrode. The bonding requirement does not specify where on the piping system.

Excuse me...."connect to that water pipe".
I thought it was pretty obvious that we were talking about a grounding electrode.
steve
 