Hi all.
Due to past experience with ground faults due to moisture or downright flooding in the fire/water service pits I have been locating the monitor modules inside the building and not inside the pit to monitor the supervisory switches for the sprinkler valves in the pit and/or PIV. I pretty much deal with addressable systems anymore, very few hard-wired systems.
Anyhow, someone told me today that you must install the modules within 3 feet of the device being monitored and that locating the addressable monitor modules remotely is a code violation.
I could not find anything in NFPA 72 re: this. I thought maybe some/all manufacturers likely have a distance limitation on wire from the module to the supervisory switch (or flow switch or whatever) but I was unaware of the 3' rule. The person who told me this said he read it in a trade mag.
Anyone?
Due to past experience with ground faults due to moisture or downright flooding in the fire/water service pits I have been locating the monitor modules inside the building and not inside the pit to monitor the supervisory switches for the sprinkler valves in the pit and/or PIV. I pretty much deal with addressable systems anymore, very few hard-wired systems.