I am looking at a project that is considering converting a plants 4.16kV solidly grounded system to a Low Resistance Grounded (LRG) system. Usually the NGR is inserted between the transformer neutral and ground at the transformer however in this case the utility wye-wye transformer is located in a vault and they will not allow the installation of any outside equipment in their vault. The utility transformer in the vault provides a 4.16kV service into a main 4.16kV Switchgar lineup.
In this case is it possible to locate the NGR outside of the vault, at the customers switchgear if the existing N-G bond at the transformer in the vault is removed? If the neutrals are brought into the 4.16kV Switchgear is it possible to insert the NGR between the 4.16kV Switchgear neutral bus and ground? In theory this seems like it would work as long as the N-G bond at the transformer is removed since any ground current would travel through ground, through the NRG back to the neutral bus and back to the neutral of the transformer.
This only potential issue I see with this is NEC code compliance regarding the required N-G bond at the service entrance switchgear (4.16kv Switchgear). Can this NGR be inserted between the Neutral and Ground bus and still count as the Main Bonding jumper per NEC?
In this case is it possible to locate the NGR outside of the vault, at the customers switchgear if the existing N-G bond at the transformer in the vault is removed? If the neutrals are brought into the 4.16kV Switchgear is it possible to insert the NGR between the 4.16kV Switchgear neutral bus and ground? In theory this seems like it would work as long as the N-G bond at the transformer is removed since any ground current would travel through ground, through the NRG back to the neutral bus and back to the neutral of the transformer.
This only potential issue I see with this is NEC code compliance regarding the required N-G bond at the service entrance switchgear (4.16kv Switchgear). Can this NGR be inserted between the Neutral and Ground bus and still count as the Main Bonding jumper per NEC?