Planning on building either a 600 or an 800 amp service to feed an outdoor event.
The service will be 120/240v 1ph.
The power company will be setting a pole at the edge of the property and its roughly 120' from the pole to where the new service equipment will be.
I had planned on an 800 amp service to a 3r MLO MDP with (6) 200 amp breakers in it and utilizing the 6 movement rule.
The Power company CT's services that are 800 amps and above so that's what I'd like to have. The Calculated load is not set in stone but they have the capability of using somewhere between 3-400 amps.
It is possible however that the Power company may only provide a 600 amp service with a 600 amp k rated meter at the pole.
I do not want to put the meter at the building where the Service Equipment will be. There's limited space at that location.
My question is if the power company does not allow the 800 amp service and provides a self contained 600 amp k rated meterbase at the pole, am I then required to set a 600 amp fused 3r disconnect at the pole ? or if we set the meter at the pole can I still consider the conductors from the meter to the MLO MDP which is 125' from the pole service conductors and leave the disconnect out?
I don't want them to have to suffer the expense of a 600 amp fused 3r disconnect at the pole if it's not required but I can't seem to find the code rule.
All of the new service equipment will be outside mounted on the side of an existing Structure and that existing structure will be refed from one of the 200amp breakers out of the MDP.
JAP>
The service will be 120/240v 1ph.
The power company will be setting a pole at the edge of the property and its roughly 120' from the pole to where the new service equipment will be.
I had planned on an 800 amp service to a 3r MLO MDP with (6) 200 amp breakers in it and utilizing the 6 movement rule.
The Power company CT's services that are 800 amps and above so that's what I'd like to have. The Calculated load is not set in stone but they have the capability of using somewhere between 3-400 amps.
It is possible however that the Power company may only provide a 600 amp service with a 600 amp k rated meter at the pole.
I do not want to put the meter at the building where the Service Equipment will be. There's limited space at that location.
My question is if the power company does not allow the 800 amp service and provides a self contained 600 amp k rated meterbase at the pole, am I then required to set a 600 amp fused 3r disconnect at the pole ? or if we set the meter at the pole can I still consider the conductors from the meter to the MLO MDP which is 125' from the pole service conductors and leave the disconnect out?
I don't want them to have to suffer the expense of a 600 amp fused 3r disconnect at the pole if it's not required but I can't seem to find the code rule.
All of the new service equipment will be outside mounted on the side of an existing Structure and that existing structure will be refed from one of the 200amp breakers out of the MDP.