Location of the Main Grounding Bus Bar in a Structured Cabling System Design

doddman1

Member
Location
Marion, IL
Occupation
RCDD
I'm designing a grounding and bonding system for an existing college from scratch as part of the structured cabling system. They have an Entrance Facilty about 100' from their Main Equipment Room or MDF which is where most of the servers and switches reside. Should the Main Grounding Bus Bar be installed at the Entrance Facility or is it okay to install it at the MDF?
 

ron

Senior Member
We typically put the principle ground bar near the entry of the Grounding Electrode System (usually near the electrical service entrance), then extend field ground bars to all needed areas.
 
Top