location of transformer for computer server room.

steve61

licensed Electrical Contracor
Location
Nebraska
Occupation
Electrician
I am installing a circuit in my place of work to have the computer server room hooked up to an emergency generator. I will be using a 15 KVA transformer to step the voltage down from 460 VAC to 208 VAC. The circuit will be about 450 feet long from the generator panel to the server room. Can I locate the transformer at the generator panel,Or do I have to have the transformer located closer to or in the server room ? Also,Do I need to install a ground rod for the transformer ? Thank You for any info. Thanks,Steve Wiese.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
For that length you would want the transformer at the end not at the beginning so that your 450' of circuiting would be at 480 volts. That solves two problems one it lowers the voltage drop and secondly you can run smaller conductors at the higher voltage.
 

steve61

licensed Electrical Contracor
Location
Nebraska
Occupation
Electrician
I already ran # 8 wire for that circuit. Maybe I could still install the transformer at the beginning of the run ? It would make it easier since I have very limited room in the server room.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I already ran # 8 wire for that circuit. Maybe I could still install the transformer at the beginning of the run ? It would make it easier since I have very limited room in the server room.
What the load on the transformer secondary? I used the Southwire VD calculator with 25 amps of load and came up with a minimum conductor size of #4.

Voltage Drop​


Minimum Conductor Size​


2.79%​

4 AWG
1 conductor per phase utilizing a 4 AWG copper conductor installed Cable, Conduit (non-Steel), & Direct Burial will limit the voltage drop to 2.79% or less when supplying 25 amps for 450 feet on a 208 volt three phase system.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
As for your question on grounding, the transformer secondary should be bonded and connected to the building grounding electrode system.
You should review 250.30 for grounding, SBJ and SSBJ
 