bryant097
Member
- Location
- new jersey
What are people thoughts on where to run the water main ground for a residential 200 amp service upgrade with the main disconnect located outside. This goes back to argument with a inspector.
Not here. While I believe the meter is the best place, especially for driven electrodes, we're not allowed because of the meter seal. That leaves the main disco enclosure.That connection can be made . . . in the POCO meter if it is on the house ahead of the Service Disconnect. There are choices.
And one of our POCOs require a rod or two at the meter.Not here. While I believe the meter is the best place, especially for driven electrodes, we're not allowed because of the meter seal. That leaves the main disco enclosure.
What are people thoughts on where to run the water main ground for a residential 200 amp service upgrade with the main disconnect located outside. This goes back to argument with a inspector.
By custom in most locations, but it can be in other locations as specified by your particular POCO.It has to go to any point between the service disconnect and the service point. The service point on an overhead service is where the drop connects to the service entrance conductors.
Welcome to the Forum.
By custom in most locations, but it can be in other locations as specified by your particular POCO.