Lock out means for Transformer primary conductors

Status
Not open for further replies.

smallfish

Senior Member
Location
Detroit
Is it stated and if so, where in the code, the need for a lock-out means for the primary feed to a transformer?

A transformer 480 to 208-120 wye was recently installed in an electrical room in a department store to feed a lighting panelboard with its own main protection. However there is no disconnecting means located in this room for the primary windings for the transformer. If the transformer supply overcurrent disconnecting means is located out-of-sight is a lock-out means integral to the switch neccessary (for worker protection)?

Thanks
 
Is it stated and if so, where in the code, the need for a lock-out means for the primary feed to a transformer?

A transformer 480 to 208-120 wye was recently installed in an electrical room in a department store to feed a lighting panelboard with its own main protection. However there is no disconnecting means located in this room for the primary windings for the transformer. If the transformer supply overcurrent disconnecting means is located out-of-sight is a lock-out means integral to the switch neccessary (for worker protection)?

Thanks

take a look at 450.14
 