LOCK OUT RELAY

Status
Not open for further replies.

JINOY JOSE

Member
Location
UAE
Occupation
ELECTRICAL TECHNICIAN
Importance of burden in Lock out relay, online every one mentioned like this,
The high burden provides greater immunity to capacitance discharge currents, which can result at the inception of an earth fault on battery wiring.
what it means?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
The lock our relay has such a large magnetic that it is not likely to operate due to the low level current that might be discharged when a fault first occurs. This provides time for the other protective devices to perform their function.
 

paulengr

Senior Member
IF you use a lockout relay practically everyone uses Electroswitch. The issue is it adds generally a one cycle delay to trip times. With today’s concerns over arc flash among other things and tighter coordination adding a lockout relay has become less popular and generally unnecessary. A good multifunction relay implements lockout in software.
 

JINOY JOSE

Member
Location
UAE
Occupation
ELECTRICAL TECHNICIAN
The lock our relay has such a large magnetic that it is not likely to operate due to the low level current that might be discharged when a fault first occurs. This provides time for the other protective devices to perform their function.
Thanks for your reply, the trip coil of the lock out relay connected in series with the protection relay contact which activates the trip command also prevents the auto reclosing .But I want to know current discharge were,and the type of fault you mentioned.
 

JINOY JOSE

Member
Location
UAE
Occupation
ELECTRICAL TECHNICIAN
IF you use a lockout relay practically everyone uses Electroswitch. The issue is it adds generally a one cycle delay to trip times. With today’s concerns over arc flash among other things and tighter coordination adding a lockout relay has become less popular and generally unnecessary. A good multifunction relay implements lockout in software.
Thanks for your reply, but apart from multifunction realy,there are other protection has used in some systems such as ITH protection in corporate with pressure flap to prevent and escape heat while flap will operate ,its limit switch will give command to LOCKOUT relay to isolate entire bus,or SWITCHGEAR during the fault.Which is not incorporate with multifunction relay.
 