Hi all,
I’ve been encountering some differing interpretations from local inspectors regarding when a lockable disconnect is required for EVSE installations.
Specifically, this concerns EVSE rated at 60 amps or less and less than 150 volts to ground.
My understanding has been based on NEC 625.43, which states:
To me, this clearly implies that only when the EVSE exceeds 60A or 150V to ground is a lockable disconnecting means required. I’ve had a few inspectors agree with that reading (some even omitting the lockable requirement entirely), presumably following 625.43.
However, a recent inspector took a different position. He stated that all EVSE installations - regardless of ampacity or voltage - require a lockable disconnect. His basis was 422.31(B), which reads:
I understand that EVSE easily exceeds 300 VA, but I question whether 422.31(B) applies, given the scope of NEC 90.3:
Since EVSE is specifically addressed in Chapter 6, wouldn’t 625.43 override or modify the general requirement from 422.31?
So here’s the core of my question:
In an EVSE installation rated 60 amps or less and under 150 volts to ground, is a lockable disconnecting means required, or does 625.43 take precedence and only require it above those thresholds?
Appreciate any clarification, and I’d especially welcome any references or experiences that might help reconcile this interpretation.
Thanks in advance for your time.
I’ve been encountering some differing interpretations from local inspectors regarding when a lockable disconnect is required for EVSE installations.
Specifically, this concerns EVSE rated at 60 amps or less and less than 150 volts to ground.
My understanding has been based on NEC 625.43, which states:
625.43 Disconnecting Means.
For EVSE and WPTE rated more than 60 amperes or more than 150 volts to ground, the disconnecting means shall be provided and installed in a readily accessible location. If the disconnecting means is installed remote from the equipment, a plaque shall be installed on the equipment denoting the location of the disconnecting means. The disconnecting means shall be lockable open in accordance with 110.25.
To me, this clearly implies that only when the EVSE exceeds 60A or 150V to ground is a lockable disconnecting means required. I’ve had a few inspectors agree with that reading (some even omitting the lockable requirement entirely), presumably following 625.43.
However, a recent inspector took a different position. He stated that all EVSE installations - regardless of ampacity or voltage - require a lockable disconnect. His basis was 422.31(B), which reads:
422.31(B) Appliances Rated Over 300 Volt-Amperes.
For permanently connected appliances rated over 300 volt-amperes, the branch-circuit switch or circuit breaker shall be permitted to serve as the disconnecting means where the switch or circuit breaker is within sight from the appliance or be capable of being locked in the open position in compliance with 110.25.
I understand that EVSE easily exceeds 300 VA, but I question whether 422.31(B) applies, given the scope of NEC 90.3:
90.3 Code Arrangement.
Chapters 1 through 4 apply generally. Chapters 5, 6, and 7 apply to special occupancies, special equipment, or other special conditions and may supplement or modify the requirements in Chapters 1 through 4.
Since EVSE is specifically addressed in Chapter 6, wouldn’t 625.43 override or modify the general requirement from 422.31?
So here’s the core of my question:
In an EVSE installation rated 60 amps or less and under 150 volts to ground, is a lockable disconnecting means required, or does 625.43 take precedence and only require it above those thresholds?
Appreciate any clarification, and I’d especially welcome any references or experiences that might help reconcile this interpretation.
Thanks in advance for your time.