M mcelweec@gmail.com CMAC1 Location NYC Occupation Electrician Nov 10, 2010 #1 If a panel is lockable can the breakers inside be considered lockable,pertaining to split ac units being fed from the condenser9
If a panel is lockable can the breakers inside be considered lockable,pertaining to split ac units being fed from the condenser9
ceb58 Senior Member Location Raeford, NC Nov 10, 2010 #2 mcelweec@gmail.com said: If a panel is lockable can the breakers inside be considered lockable,pertaining to split ac units being fed from the condenser9 Click to expand... Do what?????????????????
mcelweec@gmail.com said: If a panel is lockable can the breakers inside be considered lockable,pertaining to split ac units being fed from the condenser9 Click to expand... Do what?????????????????
Jim W in Tampa Senior Member Location Tampa Florida Nov 10, 2010 #3 If you mean as to being the means of disconnects NO unless in site but then would not need locked
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 11, 2010 #4 No, the panel or cover lock cannot be used in place of the required "lockable" individual breakers.