bphgravity
Senior Member
- Location
- Florida
What is the purpose of knowing locked-rotor current values of a motor?
For example: Lets say I have a 25 hp, 460V code A motor.
25 x 3.14 = 78.5 x 1000 / 460 / 1.732 = 98.5 amperes of locked-rotor current.
What does this tell me? Say I am using a typical inverse-time breaker. FLC is 34A x 250% = 85A breaker. Does this mean that this breaker may not hold on start-up?
For example: Lets say I have a 25 hp, 460V code A motor.
25 x 3.14 = 78.5 x 1000 / 460 / 1.732 = 98.5 amperes of locked-rotor current.
What does this tell me? Say I am using a typical inverse-time breaker. FLC is 34A x 250% = 85A breaker. Does this mean that this breaker may not hold on start-up?