locked rotor motor

Status
Not open for further replies.

luke warmwater

Senior Member
Re: locked rotor motor

In a motor, "locked-rotor" would indicate that the rotor has siezed. Are you looking for more info on this, like locked-rotor current??
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: locked rotor motor

Starting at the instant you supply power to a motor, the current will reach its very highest current in a first few milliseconds. As the motor begins to move, however slightly, the current will start to drop. When the motor has reached its cruising speed, the current will drop to its minimum value. If at that time the motor is turning a mechanical load that is equal to the motor?s rating, then the current drawn will be the figure that is known as ?Full Load Amps,? or FLA. But the peak current that is reached in a few milliseconds would stay at that level forever (or until the motor burns up), if the motor does not move. That value, known as ?Locked Rotor Current,? provides useful information (to the design engineer) about the motor?s internal resistance and about how the motor is likely to behave during a short circuit fault somewhere in the power distribution system.
 

templdl

Senior Member
Location
Wisconsin
Re: locked rotor motor

It is of my experience that as rule of thumb for the locked rotor current of a across the line squirrel cage induction motor that is 7x the motors FLA rating. However, there is an event that preceeds that which causes a spike of current current that can reach 13 times the FLA rating of the motor and 17x or more with high/energy efficient squirrel cage induction motors. It is after that spike of current that counter EMF is able to reduce the current to the LRA value.
That high spike of current can creat difficulty in keeping a MCP closed when the motor is started. Hense, you have probably noted that that issue has been reviewed and revised over art430-52 of the NEC
 

bennie

Esteemed Member
Re: locked rotor motor

NEMA Standard MG 1-1993 is a list of locked rotor current for all standard 230 volt motors.

This chart is for 230 volts,3 phase. Voltages other than 230 will have a locked rotor current inversely proportional to the voltages.
 