ibdacat Is this what your looking for?
I'm not sure if this applys to light's
230.93 Protection of Specific Circuits.
Where necessary to prevent tampering, an automatic overcurrent device that protects service conductors supplying only a specific load, such as a water heater, shall be permitted to be locked or sealed where located so as to be accessible.
I think neon is the only discharge Lighting system that has a secondary that is over 1,000 volts which would require a disconect (see 410.81), so since a disconect is not required locking the disconect closed should not matter. As the disconnect now becomes just a safty switch.
As far as certain disconnects like for fire pumps, They are required to be locked in the closed position. There is other emergency systems that require this too.
695.4 Continuity of Power.
Circuits that supply electric motor-driven fire pumps shall be supervised from inadvertent disconnection as covered in 695.4(A) or (B).
(2) Disconnecting Means. The disconnecting means shall comply with all of the following:
(1) Be identified as suitable for use as service equipment
(2) Be lockable in the closed position
(3) Be located sufficiently remote from other building or other fire pump source disconnecting means such that inadvertent contemporaneous operation would be unlikely
And when equipment is required to be Accessible (as applied to equipment). The definition states "Admitting close approach; not guarded by locked doors , elevation, or other effective means." (Pad lock's)?
And for Readily Accessible : Capable of being reached quickly for operation , renewal, or inspections without requiring those to whom ready access is requisite to climb over or remove obstacles or to resort to portable ladders, and so forth.
So if the disconnect has to be readily accessible then it has to be reached "quickly for operation" I don't think a lock would allow for that.
Then you read a artical that say's:
230.92 Locked Service Overcurrent Devices.
Where the service overcurrent devices are locked or sealed or are not readily accessible to the occupant, branch-circuit overcurrent devices shall be installed on the load side, shall be mounted in a readily accessible location, and shall be of lower ampere rating than the service overcurrent device.
so now service equipment are allowed to be locked as long as there is branch circuit breakers that the occupant can get to.