VIII. Machine Rooms, Control Rooms, Machinery Spaces, and Control Spaces
620.71 Guarding Equipment.
(A) Motor Controllers. Motor controllers shall be permitted outside the spaces herein specified, provided they are in enclosures
with doors or removable panels that are capable of being locked in the closed position and the disconnecting means is located adjacent to or is an integral part of the motor controller....
695.4 Continuity of Power. Circuits that supply electric motor-driven fire pumps shall be supervised from inadvertent disconnection as covered in 695.4(A) or (B).
(3) Disconnecting Means. All disconnecting devices that are unique to the fire pump loads shall comply with items (a) through (e).
(a) Features and Location ? Normal Power Source. The disconnecting means for the normal power source shall comply with all of the following:
(1) Be identified as suitable for use as service equipment
(2) Be lockable in the closed position ....
695.4 Continuity of Power.
(3) Disconnecting Means.
(4) Be located sufficiently remote from other building or other fire pump source disconnecting means such that inadvertent operation at the same time would be unlikely
(b) Features and Location ? On-Site Standby Generator. The disconnecting means for an on-site standby generator(s) used as the alternate power source shall be installed in accordance with 700.10(B)(5) for emergency circuits and shall be lockable in the closed position.
(e) Supervision. The disconnecting means shall be supervised in the closed position by one of the following methods:
(1) Central station, proprietary, or remote station signal device
(2) Local signaling service that causes the sounding of an audible signal at a constantly attended point
(3) Locking the disconnecting means in the closed position ....
I also believe disconnects for fire alarm systems can be locked on (perhaps in NFPA Life Safety 101)