wireman1
Senior Member
the 2008 code states in chapters 4,5 ,6 the provisions for locking or adding to the disconnecting means shall remain in place at the switch or circuit breaker whether the lock is installed or not.portable means for adding a lock to the switch or circuit breaker shall not be permitted. this appears in 410 .41 (b) ,422 31 (b) 424.19 , 430.103 and others my question is the panels are not in sight and the breakers would require a lock out means .does this mean that each breaker in the panel must have a lock out means which is approved and remain with in the panel.since the panels don,t come in with any hard ware for locking out the breakers you must order it seperately . i think square d breakers can be ordered with a lock out device attached to the breaker. i don,t know about eaton panels which are be used for this job. also stranco makes a device called circuit safe which they say is approved for panel lock out it also meets osha 1910 .147 requirments. any other suggestions would be helpful.