Lockout in lieu of disconnect

Status
Not open for further replies.

profT

Member
Location
IN
Just curious what type of lockouts you guy use when they are "permanent" on a breaker. The type with a screw that locks it in place or the one with the hole for the padlock?
 
SIE_PH_ECPLD1_s_225.jpg
shopping
shopping

I have used this style in the past. L to R Seimens, BR CH, Square D Homeline.
 
Just curious what type of lockouts you guy use when they are "permanent" on a breaker. The type with a screw that locks it in place or the one with the hole for the padlock?
While accepted as "permanent", there are none, that I really think of as permanent.

If you are referring to those that attach to the breaker handle, they are not a lockout as required by the NEC. The NEC requires a device that is attached to the breaker and remains in place with or without a lock.
 
We always used a device that could accommodate up to about six padlocks. If that was insufficient, we could attach another device in one of the six holes and so on.
 
We always used a device that could accommodate up to about six padlocks. If that was insufficient, we could attach another device in one of the six holes and so on.
The breaker locks that "snap" on to the breakers and held in by the dead front cover are lucky to stay in place with one lock on. (this applies to the typical single pole 1" wide breakers)
 