buffalonymann
Senior Member
- Location
- NC
It appears the only way to lockout medium voltage circuit breakers is to rack them out and offline of the buss. I have 4160 VAC VR 1200 amp breakers by square D
It appears the only way to lockout medium voltage circuit breakers is to rack them out and offline of the buss. I have 4160 VAC VR 1200 amp breakers by square D
Not only that, but if the vacuum bottle DOES have to interrupt a fault, the contacts can burn and despisit conductive material all over the inside of the bottle. At MV it doesn’t need to conduct very much to be lethal.Correct, it's the only safe way to do it. Keep in mind the gap in a VI is about 1/8" when the breaker is open, you want your life depending on a 1/8" gap. What if the VI loses vacuum? Do you know what the vacuum level is in your VI's? Not many plants take the time to test that and have no idea what the remaining life is.
A year later though and their safety committee is still “evaluating the concept”...
Translated as "We didn't think of that."