junkhound
Senior Member
- Location
- Renton, WA
- Occupation
- EE, power electronics specialty
OK, screwed up last summer (both me and customer).
background
Need service to new house site 870 ft up 10% grade hillsite. POCO HV line and transformer pad and one intermediate pull vault quoted at $xx last year (almost 4 figures), but was not ready to do the; digging. Customer responsible for trenching and sched 40 conduit. Luckily had bought mos conduit already. That price expired in Sept last year. NEW quote is TWICE the old one due to inflation (well OVER 4 figures). Would be even worse for customer if had not already gotten conduit for the job.
Got a 1000 ft spool of 3C 250 MCM with 1 AWG EGCs at an auction for about 12% new price, so looking at option of long run of 240 Vac.
So, the calculation question: Customer has past electric bills which run about 2500 kWhrs a month in winter, only aobut 1000 kW-hrs in summer (PNW). Is it a valid calculation to use the yearly total kW-hrs to calculate 'average' amps to determine line loss?
I think I can get the daily peaks to use, but would be easy to just use total kW-hrs to calculate line lossed and power cost.
Looked at it one way of assuming 20,000 kWhrs at 160 A, comes to line loss of 520 hours at 160 A = 1064 kW-hrs line loss (using 80 mohm line)
20 MW-hrs over 8759 hours is average of 2.3 kW; about 10 A, or 64 kW-hrs line loss
So, do I tell customer that his yearly power bill for losses would be $106 or $7? Big difference in ROI of outlay cost. Am thinking hte $7 number is more appropriate due to i^2*R ratio.
Or do I need to get customers old electric bills by the day?
background
Need service to new house site 870 ft up 10% grade hillsite. POCO HV line and transformer pad and one intermediate pull vault quoted at $xx last year (almost 4 figures), but was not ready to do the; digging. Customer responsible for trenching and sched 40 conduit. Luckily had bought mos conduit already. That price expired in Sept last year. NEW quote is TWICE the old one due to inflation (well OVER 4 figures). Would be even worse for customer if had not already gotten conduit for the job.
Got a 1000 ft spool of 3C 250 MCM with 1 AWG EGCs at an auction for about 12% new price, so looking at option of long run of 240 Vac.
So, the calculation question: Customer has past electric bills which run about 2500 kWhrs a month in winter, only aobut 1000 kW-hrs in summer (PNW). Is it a valid calculation to use the yearly total kW-hrs to calculate 'average' amps to determine line loss?
I think I can get the daily peaks to use, but would be easy to just use total kW-hrs to calculate line lossed and power cost.
Looked at it one way of assuming 20,000 kWhrs at 160 A, comes to line loss of 520 hours at 160 A = 1064 kW-hrs line loss (using 80 mohm line)
20 MW-hrs over 8759 hours is average of 2.3 kW; about 10 A, or 64 kW-hrs line loss
So, do I tell customer that his yearly power bill for losses would be $106 or $7? Big difference in ROI of outlay cost. Am thinking hte $7 number is more appropriate due to i^2*R ratio.
Or do I need to get customers old electric bills by the day?