Long distance grounding

Status
Not open for further replies.
I supplied a guesthouse off a main panel that is 310 feet in distance. Do I run my two hot conductor and grounded conductor and reestablish grounding at the guesthouse or do I have to carry a ground from the main panel?
 
Look at 250.32(B) but it depends on what code cycle you are under.

BTW under code cycle in your profile they are asking what code cycle you are under not what article you are asking about. ;)
 
Last edited:
Tucson is under the 2011 therefore you need to run 2 Ungrounded, 1 Grounded and an Equipment Grounding Conductor as well as installing a Grounding Electrode System at the sub panel location. Sounds like you will have some voltage drop considerations too.
 