nuckythompson
Member
- Location
- Nova Scotia
- Occupation
- Electrical
Hi All,
At one of our plants, there is a 4160V switchgear which is equipped with arc flash protection relays. One of the breakers on this switchgear supplies a nearby 4160-600V transformer which then feeds a 600V MCC ~1200ft away. Looking at the previous arc flash studies, cable impedance was not considered for this long run. With cable impedance considered in my calculations, if there were an arc fault at the MCC, the fault current would not be high enough to activate the arc flash protection relay on the 4160V switchgear.
I am looking for help with a solution. At this time, we are requiring 40cal gear when doing any intrusive work on long distance MCCs. One option is programming a maintenance mode into the arc flash relay which would have a lower fault level, but I am not fond of this for a few reasons (extra steps, inrush, etc.).
My questions are, have you encountered this issue in the field? Are there protection devices out there to install on existing MCCs? We are planning to get a new arc flash study done, but I am looking for answers in the meantime. Appreciate any help!
At one of our plants, there is a 4160V switchgear which is equipped with arc flash protection relays. One of the breakers on this switchgear supplies a nearby 4160-600V transformer which then feeds a 600V MCC ~1200ft away. Looking at the previous arc flash studies, cable impedance was not considered for this long run. With cable impedance considered in my calculations, if there were an arc fault at the MCC, the fault current would not be high enough to activate the arc flash protection relay on the 4160V switchgear.
I am looking for help with a solution. At this time, we are requiring 40cal gear when doing any intrusive work on long distance MCCs. One option is programming a maintenance mode into the arc flash relay which would have a lower fault level, but I am not fond of this for a few reasons (extra steps, inrush, etc.).
My questions are, have you encountered this issue in the field? Are there protection devices out there to install on existing MCCs? We are planning to get a new arc flash study done, but I am looking for answers in the meantime. Appreciate any help!