sparkyguy545
Member
Note: Possibly should be in Engineering Section
Conditions:
Buried existing conduit: 2ea 5" RMC.
Assume no add'l temperature derating necessary (30?C amb.)
Requirement:
Install 600 A Feeder in existing conduits (handholes for pulling will be added as a separate issue)
Conductors will be 90?C rated wet and dry, likely XHHW-2, or RHW-2
Termination lugs at end will be rated 75?C
Distance 1800 feet
Allow Maximum 3% VD
System" 480 V, 3-phase, 3-wire plus supplemental equipment gnd cond. (no neutral).
Comp assistance for feeders and EGC including allowances for VD.
I've done this two ways, and get two different answers for cable make-up.
Before it's suggested, the project space at the ends does not allow step-up, step-down xfmrs. I'm stuck with the 5" pipe.
Conditions:
Buried existing conduit: 2ea 5" RMC.
Assume no add'l temperature derating necessary (30?C amb.)
Requirement:
Install 600 A Feeder in existing conduits (handholes for pulling will be added as a separate issue)
Conductors will be 90?C rated wet and dry, likely XHHW-2, or RHW-2
Termination lugs at end will be rated 75?C
Distance 1800 feet
Allow Maximum 3% VD
System" 480 V, 3-phase, 3-wire plus supplemental equipment gnd cond. (no neutral).
Comp assistance for feeders and EGC including allowances for VD.
I've done this two ways, and get two different answers for cable make-up.
Before it's suggested, the project space at the ends does not allow step-up, step-down xfmrs. I'm stuck with the 5" pipe.