Wasn't sure if this should be posted here or in engineering, but since the discussion centers around cost I put it here.
Hypothetical scenario:
Need to run 600 amps of 480v 3ph 4w 500-600ft (along a somewhat challenging path, vertically through a building, across a roof, and back down the other side). Is this enough current and a long enough run to where it would make sense to step up to 4160v and back down to 480v at the other end? This would cut three conduits down to one smaller one, eliminate a ton of coring, and get rid of the neutral needed with a 480v feeder. The unit substations would be located indoors.
If my quick assumptions are correct, the 480v circuit would require 3 parallel sets of 4x 4/0 cu (lets say specs forbid aluminum). Thats $25,000 in wire not counting a EGC. The 4160v using 3x #6 MV-105 is $3600 in wire again not counting a EGC.
How much does a 500kva unit substation cost?
At the step down end if there are substantial loads at both 120/208 and 480v does it make sense to use two smaller unit substations to step down directly to the utilization voltage?
On the step up end, all that would be needed is the transformer and a 4160v disconnect on its output correct? The breaker in the switchgear supplying it can be the primary disco / ocpd correct?
How would the transformer core losses compare, say 500kva 480-4160 + 300kva 4160-120/208 + 112kva 4160-277/480 VS: 300kva 480->120/208?
Hypothetical scenario:
Need to run 600 amps of 480v 3ph 4w 500-600ft (along a somewhat challenging path, vertically through a building, across a roof, and back down the other side). Is this enough current and a long enough run to where it would make sense to step up to 4160v and back down to 480v at the other end? This would cut three conduits down to one smaller one, eliminate a ton of coring, and get rid of the neutral needed with a 480v feeder. The unit substations would be located indoors.
If my quick assumptions are correct, the 480v circuit would require 3 parallel sets of 4x 4/0 cu (lets say specs forbid aluminum). Thats $25,000 in wire not counting a EGC. The 4160v using 3x #6 MV-105 is $3600 in wire again not counting a EGC.
How much does a 500kva unit substation cost?
At the step down end if there are substantial loads at both 120/208 and 480v does it make sense to use two smaller unit substations to step down directly to the utilization voltage?
On the step up end, all that would be needed is the transformer and a 4160v disconnect on its output correct? The breaker in the switchgear supplying it can be the primary disco / ocpd correct?
How would the transformer core losses compare, say 500kva 480-4160 + 300kva 4160-120/208 + 112kva 4160-277/480 VS: 300kva 480->120/208?