Strombea
Senior Member
- Location
- Prescott, Arizona, USA
We are designing and installing 2 lights and 1 receptacle in each unit in a 80 unit building that is 600 ft long. The customer wants each unit on its own 20 amp breaker and they won’t budge. my original design is that the units within 100 ft get #12 MC, the units from 100 ft to 250 ft get #10 MC but per my math, after 250 ft I should be at #8 and towards the end of the 600ft I should be using #6. So I had designed a 240v to 480v step up TX @ 50kva that served a 480v 100 amp panel, each home run(unit) would then get its own step down 3kva TX mounted in the unit, fed from the 2 pole 480v, this allowed me to still use #10
FYI I’m using 15 amps at end of run and 5% max VD , no continuous loads.
there is No where to add a sub panel in the building as they want all units for rent income and there is only 24” between roll up doors on the face, so I can’t do a sub panel anywhere it seems. The step down tx are around 300$ each @ 40 units is around $12,000 extra to not have to use #8 and #6 wire
any suggestions???
FYI I’m using 15 amps at end of run and 5% max VD , no continuous loads.
there is No where to add a sub panel in the building as they want all units for rent income and there is only 24” between roll up doors on the face, so I can’t do a sub panel anywhere it seems. The step down tx are around 300$ each @ 40 units is around $12,000 extra to not have to use #8 and #6 wire
any suggestions???