This is a long shot gentlemen but if anyone has any insight I would certainly appreciate it.
been asked by a client to look at why they are having problems with 4, 208, 3ph, N and Ground, L21-30R circuits each of which is feeding a TSE Climatic Chamber in a vivarium. These Chambers among other things are temperature controlled and may be set to anything between 22 deg C and 30 deg C.
am trying to get a wiring diagram but so far not getting a lot of corporation from the vendor.
So we've put a meter on these things, and the amp values are all over the map. As it is heating or cooling (which ought to represent the worst case current draw), first of all phase A will go to maybe 12amps but it keeps bouncing from near zero then back up to the 12 amps. Phase B goes up to around 7Amps and also bounces and then phase C has nothing.
What's even stranger is that the brand new square D panelboard is arcing on the line side of each of these 4 breakers seemingly on phase B. I guess it could be a problem with the panelboard but I can't help but to think it's somehow related to these damn chambers.
Has anyone ever run into something like this?
Thanks,
Mike
been asked by a client to look at why they are having problems with 4, 208, 3ph, N and Ground, L21-30R circuits each of which is feeding a TSE Climatic Chamber in a vivarium. These Chambers among other things are temperature controlled and may be set to anything between 22 deg C and 30 deg C.
am trying to get a wiring diagram but so far not getting a lot of corporation from the vendor.
So we've put a meter on these things, and the amp values are all over the map. As it is heating or cooling (which ought to represent the worst case current draw), first of all phase A will go to maybe 12amps but it keeps bouncing from near zero then back up to the 12 amps. Phase B goes up to around 7Amps and also bounces and then phase C has nothing.
What's even stranger is that the brand new square D panelboard is arcing on the line side of each of these 4 breakers seemingly on phase B. I guess it could be a problem with the panelboard but I can't help but to think it's somehow related to these damn chambers.
Has anyone ever run into something like this?
Thanks,
Mike