Based on the meggering question.
How many of you have come across issues that most likely existed for years un-noticed yet were only moments away from a fault.
Such as:
We did a demo on a kitchen in the 70's of a house built in the 50's, a nail had been driven into the rag-wire SEC and knicked a phase conductor yet never hit the stranded ground the nail was energized.
Parallel feeders 3-sets 500kcmil in PVC to a chiller "A" phase in one conduit, "B" phase in another conduit and "C" phase in the 3rd conduit, no slots cut in the cabinets (MDP or chiller cabinet) the insulation was GONE/burnt off all conductors for two feet in each direction yet never shroted (no contact with each other or ground), building was 20 years old.
How many of you have come across issues that most likely existed for years un-noticed yet were only moments away from a fault.
Such as:
We did a demo on a kitchen in the 70's of a house built in the 50's, a nail had been driven into the rag-wire SEC and knicked a phase conductor yet never hit the stranded ground the nail was energized.
Parallel feeders 3-sets 500kcmil in PVC to a chiller "A" phase in one conduit, "B" phase in another conduit and "C" phase in the 3rd conduit, no slots cut in the cabinets (MDP or chiller cabinet) the insulation was GONE/burnt off all conductors for two feet in each direction yet never shroted (no contact with each other or ground), building was 20 years old.