Yes, the question is on top: Would I be allowed to use #8 THHN copper wire instead of #6, if my appliance at the attic has wire terminals rated for 75C ?Boy I never knew NM has an ampacity of 60 C.
What book is that?
BTW is there a question here?
I ask the same as Bob. What is that book ?
They totally overlook that NM has 90? conductors as far as derating in concerned..
You may use a #8, in fact, I see no problem with the #10.
Yes, the question is on top: Would I be allowed to use #8 THHN copper wire instead of #6, if my appliance at the attic has wire terminals rated for 75C ?
I don't know what book it is. It just ended up in my hands somehow.
Roger, I don't agree with the temp.I say the book is correct.
What is happening is we must "adjust" the ampacity of the load to the heat in the attic (122 deg F) which becomes 43 amps, now 334.80 tells us that if we do use the 90 deg rating for "derating" purposes the conductor can not exceed 60 deg column but, we are not derating the cable (there are only three conductors in this cable) so we must use the 60 deg column straight up for theadjusted load
Meaning, a # 8 is only good for 40 amps so the # 6 is correct.
BTW, the book is pre 2002.
Roger
I concur with #10 but I must state that I have never seen anyone use the ambient temp chart for resi work. 120 degree ambient is pretty hot. Sure most attics will get that hot but again what does ambient temp. mean?
Roger, I don't agree with the temp.
The highest it ever reached isn't the ambient, is it?
I say the book is correct.
What is happening is we must "adjust" the ampacity of the load to the heat in the attic (122 deg F) which becomes 43 amps, now 334.80 tells us that if we do use the 90 deg rating for "derating" purposes the conductor can not exceed 60 deg column but, we are not derating the cable (there are only three conductors in this cable) so we must use the 60 deg column straight up for theadjusted load
Meaning, a # 8 is only good for 40 amps so the # 6 is correct.
BTW, the book is pre 2002.
Roger
Yes, I think the book was before or around 2002. What do you think about my question?
"Would I be allowed to use #8 THHN copper wire instead of #6, if my appliance at the attic has wire terminals rated for 75C ?"
Todd, I would say the highest temp would be the true ambient for the question as it is presented. We would have to answer the question with the information given and after the adjustment, we would be looking at 43 amps
Roger
First off it is an a/c unit so it would be outside. Yes you could use #8 but I believe a #10 would also get it. Here is why.Yes, I think the book was before or around 2002. What do you think about my question?
"Would I be allowed to use #8 THHN copper wire instead of #6, if my appliance at the attic has wire terminals rated for 75C ?"
Roger, I still agree with Dennis.
#10 NM @90? is 40 amps. In a 122? ambient the multiplier is 82 thus 32.8 amps.
The 60? rating is 30 so we can use whichever is less.
The load is 25 amps (or possibly 25 x 1.25).. less than the 30 amp ampacity of #10
Roger, I still agree with Dennis.
#10 NM @90? is 40 amps. In a 122? ambient the multiplier is 82 thus 32.8 amps.
The 60? rating is 30 so we can use whichever is less.
The load is 25 amps (or possibly 25 x 1.25).. less than the 30 amp ampacity of #10
Gus, everybody is trying to derate the conductor, what we need to do is adjust the load ampacity and size the conductors to it, I still go with the book being correct.
Roger