s-park-er
Member
- Location
- Oroville, CA
- Occupation
- Building mechanic - specialty problem-solver.
I just want to confirm before pulling...
This project is interesting and keeps getting more so - the owner is an impulse buyer of building materials; he finds great deals but not always what is needed, so he modifies the plan to accommodate sometimes. Here's the latest. POCO drop is at roadside, 400A to two 200's (house and shop). House is 250ft pull in 3" PVC. at the start he told me that he has 4/0 wire to pull to the house panel (which we will be changed for the correct one for those who saw my last post). I assumed copper, but I was wrong! So, after convincing him that we cannot use the aluminum as he planned, we looked at options. Buying new copper $$$$$ yikes!! Buying the correct size AL $$$$ also yikes! but alas, he has PLENTY of the Al 4/0; Thousands of feet!!! Sooooo.... we are going to pull parallels of that and call it good.
I'd just like to be certain of my assumption that we can use a SINGLE 4/0 AL for the grounded circuit conductor (neutral) Quick load calcs come up with ~~133A, with 200A OCPD at each end, and we will be using #2CU EGC (which he found somewhere for a deal...)
Thanks in advance, you all are great!!
This project is interesting and keeps getting more so - the owner is an impulse buyer of building materials; he finds great deals but not always what is needed, so he modifies the plan to accommodate sometimes. Here's the latest. POCO drop is at roadside, 400A to two 200's (house and shop). House is 250ft pull in 3" PVC. at the start he told me that he has 4/0 wire to pull to the house panel (which we will be changed for the correct one for those who saw my last post). I assumed copper, but I was wrong! So, after convincing him that we cannot use the aluminum as he planned, we looked at options. Buying new copper $$$$$ yikes!! Buying the correct size AL $$$$ also yikes! but alas, he has PLENTY of the Al 4/0; Thousands of feet!!! Sooooo.... we are going to pull parallels of that and call it good.
I'd just like to be certain of my assumption that we can use a SINGLE 4/0 AL for the grounded circuit conductor (neutral) Quick load calcs come up with ~~133A, with 200A OCPD at each end, and we will be using #2CU EGC (which he found somewhere for a deal...)
Thanks in advance, you all are great!!