Looking for input. I went with a GC to look at a small job at a small nutrition supplement manufacturer. The job was a recent tenant finish in an industrial park, and previous electrician is done and has final inspection passed. Now I'm here to hook up some equipment. It's all cut and dry, except this....
They have a whole host of HEPA filters running through control boxes protruding into a mezzanine. I guess the owner gave specs to the previous electrician for 120v 20a units, so there are a half dozen circuits wired with MC cable into the walls above
But the control boxes that got installed are 120v and 28 amps. There are 5 of those control boxes. So I have to add 5 circuits. No biggie.
There is a 200 amp 42 space panel that's full, almost all small 3-phase loads (most are 20 amp breakers). Nothing is labeled, but I know there are 2 air compressor circuits on 3-pole 30 amp breakers. Equipment is not there yet
To the left is a newly added 24 space panel that's full of mostly single breakers. Nothing is labeled. That panel is powered by a 2-pole 100-amp breaker in spaces 1 & 3 of the main panel.
Here's what I told GC....
The main panel is out of space, so I can't add the 5 there. I have 4 spaces in the subpanel, but....
Considering the main panel is full of 3-phase loads, previous electrician should have never added a single phase panel. How could it ever be balanced?
There's substantial load in those HEPA filters. If I add 3 on one leg, thats 84 amps. I don't know what all those other single circuits are powering, and can't measure amperage until they're up and running. But they can't get up and running without the filters.
I think it needs to have that subpanel changed to a 30-space 3-ph panel. In order to do that, I would need to put a tandem breaker for the 2 single pole circuits in the main panel, then shift a 3-pole breaker down one space to make room for a 3-pole 100 amp breaker. I don't think the panel is rated for more than 42 circuits.
Either that, or add a second subpanel to the left of the what's in the pic. Then I'd have to move a 3-pole circuit from the main panel into new subpanel.
I think I've been clear about my preference, but what do you think? With that kind of info, what would you suggest?
They have a whole host of HEPA filters running through control boxes protruding into a mezzanine. I guess the owner gave specs to the previous electrician for 120v 20a units, so there are a half dozen circuits wired with MC cable into the walls above
But the control boxes that got installed are 120v and 28 amps. There are 5 of those control boxes. So I have to add 5 circuits. No biggie.
There is a 200 amp 42 space panel that's full, almost all small 3-phase loads (most are 20 amp breakers). Nothing is labeled, but I know there are 2 air compressor circuits on 3-pole 30 amp breakers. Equipment is not there yet
To the left is a newly added 24 space panel that's full of mostly single breakers. Nothing is labeled. That panel is powered by a 2-pole 100-amp breaker in spaces 1 & 3 of the main panel.
Here's what I told GC....
The main panel is out of space, so I can't add the 5 there. I have 4 spaces in the subpanel, but....
Considering the main panel is full of 3-phase loads, previous electrician should have never added a single phase panel. How could it ever be balanced?
There's substantial load in those HEPA filters. If I add 3 on one leg, thats 84 amps. I don't know what all those other single circuits are powering, and can't measure amperage until they're up and running. But they can't get up and running without the filters.
I think it needs to have that subpanel changed to a 30-space 3-ph panel. In order to do that, I would need to put a tandem breaker for the 2 single pole circuits in the main panel, then shift a 3-pole breaker down one space to make room for a 3-pole 100 amp breaker. I don't think the panel is rated for more than 42 circuits.
Either that, or add a second subpanel to the left of the what's in the pic. Then I'd have to move a 3-pole circuit from the main panel into new subpanel.
I think I've been clear about my preference, but what do you think? With that kind of info, what would you suggest?