hardworkingstiff
Senior Member
- Location
- Wilmington, NC
I just received a set of plans for a marina to bid. The plans show a #4 type W cable feeding a power center with (2) 50-amp receptacles. This is a common wiring practice in this area and I've done it many times. Last year I discovered we are not compliant with 310.14(C) because we are using the ampacities of Table 400.5(B) (with our application the #4 at 75c is rated 115-amps) and not Table 310.16 (which at 75c is rated 85-amps).
With competition the way it is (others will be bidding this) and I'm pretty sure the AHJ in this area will not catch this issue would you just bid it this way or would you bring it up and cause a fuss and ruckus?
With competition the way it is (others will be bidding this) and I'm pretty sure the AHJ in this area will not catch this issue would you just bid it this way or would you bring it up and cause a fuss and ruckus?