brycenesbitt
Senior Member
- Location
- United States
I am calculating for #10 ungrounded and #12 grounded THWN-2 90C wire in existing 1" PVC conduit that's in a
ground level commercial poured concrete slab with no insulation.
That conduit then transitions to metal at the slab edges.
The desired fill works with NEC Section 310.15 if using the 104% correction factor for the "ambient temperature",
followed by de-rating for the number of conductors in the conduit.
The local soil temperature at:
Shows a range typical 45F to low 50F. The ten year monthly peak average is 52F. But this past year
it's been warmer, and soil temperatures have risen to as much as 60F, as the area climate is warming by all measures.
I saw this old closed thread:
https://forums.mikeholt.com/threads/how-can-i-determine-ambient-temperature.76033/
Is there any update on what's considered fair game for ambient temperature for underground slab conduit, and it's short stub above the slab?
Would you consider it fair game to up the ampacity of the THWN-2 by 4% in this situation? Am I reading all the above correctly?
ground level commercial poured concrete slab with no insulation.
That conduit then transitions to metal at the slab edges.
The desired fill works with NEC Section 310.15 if using the 104% correction factor for the "ambient temperature",
followed by de-rating for the number of conductors in the conduit.
The local soil temperature at:
Soil Temparature Maps | GreenCast | Syngenta
www.greencastonline.com
Soil Temperature
This app provides soil temperature and moisture data and forecasts for horticulture, agriculture and gardening.
soiltemperature.app
🌤️ Free Open-Source Weather API | Open-Meteo.com
Open-Source ☀️️️️️️️️️️️️️️️️️️️️️️️️️️️️️ Weather API with free access for non-commercial use. No API Key required ✅. Accurate weather forecasts for any location. Open-Meteo provides high-resolution open data ranging from 1 to 11 kilometers from national weather services. With a user-friendly...
open-meteo.com
Shows a range typical 45F to low 50F. The ten year monthly peak average is 52F. But this past year
it's been warmer, and soil temperatures have risen to as much as 60F, as the area climate is warming by all measures.
I saw this old closed thread:
https://forums.mikeholt.com/threads/how-can-i-determine-ambient-temperature.76033/
Is there any update on what's considered fair game for ambient temperature for underground slab conduit, and it's short stub above the slab?
Would you consider it fair game to up the ampacity of the THWN-2 by 4% in this situation? Am I reading all the above correctly?