If fuses regularlly 'opened' due to loose connections, we wouldn't need to infrared scan them.We kept having a fuse blow on phase A of a 3 phase HVAC unit. I found a loose connection at the disconnect above the fuse that kept blowing. I believe the fuse blew because of heat from the arc rather than overcurrent. Is this true.
We kept having a fuse blow on phase A of a 3 phase HVAC unit. I found a loose connection at the disconnect above the fuse that kept blowing. I believe the fuse blew because of heat from the arc rather than overcurrent. Is this true.
Loose connection on line side of disconnect often doesn't have enough heat make it to the fuse to blow the fuse. May want to make sure the switch is not the weak connection and the loose lug was a casualty of the heat. If so the problems are not over. If the lug or switch blades are discolored the problems are not over either.
The loose connection drew more current on that phase. So yes, the fuse failed because of overload.
How would a loose connection cause more current flow?
The energy to create the heat had to come from somewhere.
The energy to create the heat had to come from somewhere.
Thank you for all your input. I changed out the disconnect and will post later the results. I do have a question in relation though. How does a loose connection cause more current flow. In theory isn't the loose connection acting as a resistor to current.
Thank you for all your input. I changed out the disconnect and will post later the results. I do have a question in relation though. How does a loose connection cause more current flow. In theory isn't the loose connection acting as a resistor to current.