This might be a no Brainer , but here it goes anyway, can a lose connection to a breaker, make that breaker trip thanks, I have a oven on a 30 Amp beaker it was tripping on the home owner connection was lose arching thanks
This might be a no Brainer , but here it goes anyway, can a lose connection to a breaker, make that breaker trip thanks, I have a oven on a 30 Amp beaker it was tripping on the home owner connection was lose arching thanks
Without a doubt. Guilty.I've seen it happen.
It is not especially likely, but it is possible.
The arcing does generate a small amount of heat but the copper wires are very efficient heat sinks.
I would not be counting on it as a safety measure though it could happen.
I would be more inclined to suspect that the arcing was causing surges of startup current that might be what is actually tripping the breaker, as opposed to the heat being generated by the arc itself.
Well, the resistance of metal goes up with temperature. It seems to me that a resistive heating element will draw more current when you first turn it on (when it is cold) than it will when it comes up to working temperature.An oven is a purely resistive load. Where would the inrush be coming from?
Well, the resistance of metal goes up with temperature. It seems to me that a resistive heating element will draw more current when you first turn it on (when it is cold) than it will when it comes up to working temperature.
Well, the resistance of metal goes up with temperature. It seems to me that a resistive heating element will draw more current when you first turn it on (when it is cold) than it will when it comes up to working temperature.
So a 200 watt light bulb pulls about 1.6 amps at it's operating temperature. When cold, the inrush is about 15X steady state so about 24 amps. Usually you don't trip a 15 amp breaker when you turn on a 200 watt lamp, because the inrush is only for a few cycles. I would think the same principal applies to the oven and therefore you shouldn't expect an issue under normal circumstances.
Negligible for an oven.
Copper: 4E-3 deg C
NiChrome: 0.17E-3 deg C, not much change hot from cold.
Carbon: -0.5 E-3 deg C, lower R with temp.
It is not especially likely, but it is possible.
The arcing does generate a small amount of heat but the copper wires are very efficient heat sinks.
I would not be counting on it as a safety measure though it could happen.
I would be more inclined to suspect that the arcing was causing surges of startup current that might be what is actually tripping the breaker, as opposed to the heat being generated by the arc itself.
FWIW, the heating element in an oven does not come up to working temperature nearly as quickly as does the filament of an incandescent light bulb, but I agree, it's not likely to trip a breaker.You are correct, the cold inrush of the heating element should not trip the breaker, even so it would be in the first few hundred milliseconds.
FWIW, the heating element in an oven does not come up to working temperature nearly as quickly as does the filament of an incandescent light bulb, but I agree, it's not likely to trip a breaker.