losing c phase (NEED HELP)

Status
Not open for further replies.
I have a 100 amp panel that is fed from a 100 amp switch. Tha panel feeds 2 a/c units. I keep losing C phase(fuse is blowing). Any suggestions on where to start my troubleshooting? Thx.
 
loose connections: look for heat (discoloration, IR scan, thermography, etc)

high impedance fault (amprobe)

intermittant fault (megger, monitor)
 
Are you actually checking the fuses or just voltage on the load end? I had a fused disconnect once that would lose a phase. I immediately assumed blown fuse ( no voltage to ground on load end). after 6 or seven fuse changes over a 2 day period I found out that I had a loose fuse clip. When i plugged a new fuse in it would make contact for a few hours.
 