inspector 102
Senior Member
- Location
- Northern Indiana
At our local park ground, there is a pavillion that when the breakers are off, there appears to be 120 volts to panel, but breakers are turned on, voltage drops to about 75 volts. As an inspector, I told them it appears they lost a nuetral, but where would they start looking, supply side or load side of breaker. Any thoughts on how to locate break underground. Megger is the only way I could think of without smoke coming out of the ground. Thanks for any guidance.
